What Size Fuse Should I Use for My 48V Inverter?

0
Asked By FuzzyBee42 On

I'm trying to figure out the right fuse size for my 48V inverter, which is rated for 2000 watts continuously and can peak at 4000 watts. Based on what I've read, I think I need a 60 amp fuse, but I'm not sure what type of fuse I should use. Can anyone offer advice?

2 Answers

Answered By MotorGuru On

If you plan to run electric motors or anything with a motor start-up, keep in mind they often pull a lot more current at start-up. If that's the case, you might trip fuses more often than you'd like, especially with your air conditioner being a peak load. Just make sure to overestimate a bit, so you don't run into issues.

Answered By TechWhiz123 On

It's always best to check the manufacturer's manual first; it should give you the specific recommendations for fuse size and wiring. Generally, if you calculate it out, for a 4000W inverter you’d be looking at about 104 amps for continuous use, but if you're just using it at 2000W then a 60-amp fuse is likely sufficient. I’d recommend a 60 amp Class T fuse close to the batteries, as those are durable and can handle large fault currents without issues.

InverterEnthusiast -

Sounds good! What about using a Mega Fuse for those lower amps?